Enron Modbus Driver
Not counted towards your tag license limit.
Enron Modbus is a variation on the standard Modbus protocol that allows for the transmission of stored historical data and alarm/event logs. The standard read/write Modbus function codes, 01, 03, 05, 06, are supported and used to read or write real-time values. The only major difference between accessing real-time values in regular Modbus versus Enron Modbus is the register addressing. See the addressing section for details.
Many devices that communicate via Enron Modbus also maintain an internal historical log with periodic, hourly or daily records. Additionally, they usually have a separate log, which contains alarm and event data specific to the flow calculations that the device is monitoring. The Enron driver allows both of these logs to be read and then transferred to the VTScada historian.
Related application properties:
The following property settings hold additional configuration parameters for your Enron Modbus driver:
EnronBoolMaxBlockSize - Maximum number of standard Boolean values requested in a single read.
EnronShortMaxBlockSize - Maximum number of standard short integer values requested in a single read.
EnronLongMaxBlockSize - Maximum number of standard long integer/floating point values requested in a single read.
EnronMaxHistoryBlockSize - Maximum number of historical values requested in a single history log read.
EnronPropogateOnlyOnDataChange - If set, don't bother processing incoming data if it hasn't changed since the last read. Note that this setting does not apply to history reads or event log reads (which are always processed).
EnronSharedRPC - Set to use the same RPC service for all instances of the Enron Modbus driver. drivernameSharedRPC properties are stored in Settings.Startup, not Settings.Dynamic. Changes require a restart of the application in order to take effect.
EnronContinuousHistoryRead - When set, a single history poll cycle will continue reading from the device until all new history has been read.
EnronHistoryReadStartUpDelay - Seconds to wait for Enron history tags to initialize before timing out with a comms error.
The ID tab of every tag includes the same common elements: Name, Area, Description, and Help ID.
Name:
Uniquely identifies each tag in the application. If the tag is a child of another, the parent names will be displayed in a separate area before the name field.
You may right-click on the tag's name to add or remove a conditional start expression.
Area
The area field is used to group similar tags together. By defining an area, you make it possible to:
- Filter for particular tag groups when searching in the tag browser
- Link dial-out alarm rosters to Alarm tags having a particular area
- Limit the number of tags loaded upon startup.
- Filter the alarm display to show only certain areas.
- Filter tag selection by area when building reports
When working with Parent-Child tag structures, the area property of all child tags will automatically match the configured area of a parent. Naturally, you can change any tag's area as required. In the case of a child tag, the field background will turn orange to indicate that you have applied an override.
To use the area field effectively, you might consider setting the same Area for each I/O driver and its related I/O tags to group all the tags representing the equipment processes installed at each I/O device. You might also consider naming the Area property for the physical location of the tag (i.e. a station or name of a landmark near the location of the I/O device). For serial port or Roster tags, you might configure the Area property according to the purpose of each tag, such as System or Communications.
You may define as many areas as you wish and you may leave the area blank for some tags (note that for Modem tags that are to be used with the Alarm Notification System, it is actually required that the area field be left blank).
To define a new area, type the name in the field. It will immediately be added. To use an existing area, use the drop-down list feature. Re-typing an existing area name is not recommended since a typo or misspelling will result in a second area being created.
There is no tool to remove an area name from VTScada since such a tool is unnecessary. An area definition will exist as long as any tag uses it and will stop existing when no tag uses it (following the next re-start).
Description
Tag names tend to be brief. The description field provides a way to give each tag a human-friendly note describing its purpose. While not mandatory, the description is highly recommended.
Tag descriptions are displayed in the tag browser, in the list of tags to be selected for a report and also on-screen when the operator holds the pointer over the tag’s widget. For installations that use the Alarm Notification System, the description will be spoken when identifying the tag that caused the alarm.
The description field will store up to 65,500 characters, but this will exceed the practical limits of what can be displayed on-screen.
This note is relevant only to those with a multilingual user interface:
When editing any textual parameter (description, area, engineering units...) always work in the phrase editor. Any changes made directly to the textual parameter will result in a new phrase being created rather than the existing phrase being changed.
In a unilingual application this makes no difference, but in a multilingual application it is regarded as poor practice.
Help Search Key
Used only by those who have created their own CHM-format context sensitive help files to accompany their application.
Server List
Select (or create) a named server list.
Enron Modbus Driver properties Options
Comm Channel
Choose the format of the outgoing messages. Serial RTU sends the messages as they are and includes a CRC
Cyclic Redundancy Check at the end. Open Modbus TCP prefaces the messages with a TCP header. Note that the comm channel setting can be changed independently of the port tag. For example, some devices use the Serial RTU protocol sent out over a TCP/IP port.
Squelch Noise Present
Applies when communicating over a radio modem. Select this box to enable squelching of background noise.
Squelch Time
The number of seconds to wait before clearing noise when the Squelch Noise Present option has been selected.
Store Last Output Values
When selected, the driver will maintain a record of the last value written to each output address. This may be useful in at least two situations:
- For hardware that does not maintain its state during a power loss and must be restored to that state when re-started.
- When failed hardware is replaced by a new device and you would like to start that device with the values last written to the old one.
If the last output values are stored, they may be re-written by either of two methods:
- Automatically, when communication is restored to the device.
- Manually by way of a button press. See, Rewrite Outputs Widget for details.
Changing this value from selected to deselected will cause all stored values to be erased immediately.
If this driver is being used in conjunction with a Driver Multiplexer, then configure the Driver Multiplexer to store the last values, not the drivers connected to the Multiplexer. In this case, only the Multiplexer should be configured to re-write automatically.
Enable Auto Rewrite
If selected, the Store Last Output Values option will also be activated. This option causes the driver to rewrite the last value written to each output, in the event that communications are lost and then restored.
Use this option only if you are certain that you want the last values to be rewritten automatically after an interruption in driver communications.
Device Clock Time Zone
The time zone of the clock in the Enron Modbus device. This is used to correct the time-stamped values read from the device by VTScada for storage in its historian using UTC format. Regardless of the time zone selected with this option, the driver assumes that the device does NOT adjust its clock for daylight savings time (DST).
- Uses Server Time Zone (no DST) - assumes that the device is in the same time zone as the server.
- Device Clock In UTC - the clock in the device is set to UTC
- Actual Time Zone - select the time zone where the device is located.
Enron Modbus Driver Configuration - Communications
Port
The port tag through which this driver communicates to a device, usually either a serial port tag or a TCP/IP tag.
Time-Out Limit
The length of time, in seconds, that the driver should wait for a reply from the device.
Retries
The number of times to retry a message before declaring an error.
Use only if the driver is connected to a Serial port. When using TCP/IP, do not set to any value other than 0.
Hold
Check this to have I/O tags attached to the driver hold their last value in the event of a communication failure. If not checked, tags will have their value set to invalid on a communication failure.
RTS Key Off Delay
Used for serial communications, this field represents the length of time in seconds that the device will wait before dropping RTS at the end of a data transmission.
Modbus Address
The Modbus address of the Enron Modbus device.
Retry Delay
The length of time, in seconds, that the driver will wait between retry attempts if there is no reply to the initial message.
Enron Modbus Driver Configuration - Protocol
Operator Change / Alarm Event Log...
Base Date
When operator-change or alarm-event-log, time-stamped data is returned from the device, the year is provided as a two-digit number. That number is then added to this base date to produce the actual date used for the timestamp. for example, if the number returned was "34" and the base date is "1980" then the year will be recorded as 2014. This information should be available in your device's documentation.
Date Returned Before Time
Usually operator-change or alarm-event-log time-stamps from the device are returned with the time being sent before the date. If the reverse is true for your device then this box should be selected.
History Log...
Base Date
When history log time stamped data is returned from the device, the year is provided as a two-digit number. That number is then added to this base date to produce the actual date used for the timestamp (e.g. if the number returned was "34" and the base date is "1980" then the year will be re-corded as 2014. This information should be available in your device's documentation.
Date Returned Before Time
Usually, history-log time-stamps from the device are returned with the time being sent before the date. If the reverse is true for your device then this box should be selected.
Enable Multi-Write Function
Although standard Modbus multi-write function codes are not defined as part of the Enron Modbus standard, some devices can make use of them. If this is true of your device, this box may be selected.
Enron Modbus Driver Configuration - History
The Enron Modbus protocol allows for the retrieval of historical data records stored in the device. Each record holds the value of several variables for a specific timestamp, ordered by an incrementing index value. The following table is a representation of a theoretical hourly history log.
| Index | Date | Time | Temperature | Pressure | Flow |
|---|---|---|---|---|---|
| 1 | 08/08/2014 | 08:00:00 | 21.3 | 87.2 | 48.4 |
| 2 | 08/08/2014 | 09:00:00 | 22.4 | 86.9 | 49.4 |
| 3 | 08/08/2014 | 10:00:00 | 25.1 | 87.3 | 48.7 |
| ... | ... | ... | ... | ... | ... |
| 1024 | 27/06/2014 | 19:00:00 | 18.9 | 87.4 | 44.0 |
Every hour, a new record is created inside the device. After the final history register has been filled (in this case index 1024) the next record goes back to index 1 and overwrites the record stored there.
The History tab is used to define and to track the characteristics and status of the device's history log. The "table columns" that are to be logged should be defined here. Up to 30 log tables may be defined.
History Address Number
Select which of the 30 separate history addresses to configure.
Log Address
The register address in the device where the history log is stored. For the first flow run, this is usually either 701 (for hourly history) or 702 (for daily history).
Default values of 701 through 710 are provided for History Address Numbers 1 through 10.
History Log Index Address
Some devices track the position of the index of the next record to be written. The address where this index position is stored should be entered here. This field is only used if the Enron driver's Read History Index from a Separate Address box is selected.
Total Number of Log Indices
The total number of records stored in the history log. After the driver has read this many indices it will start back at the first index.
Log Indices Begin at 0
Select this box if the first index of your device is 0 instead of 1.
Read History Log Index from a Separate Address
Historical data is read from a table in the device, which is ordered by an index value. By default the Enron Modbus driver will read all indices sequentially until arriving at the end of the new data (according to the datum's timestamp), however some devices track the most recent index value internally in a separate register. If this is the case with your device then this box should be selected. Note that the actual index register is set as part of the Enron History tag.
Use a 6-Byte Time/Date Format
The Enron Modbus protocol it returns the time and date from history logs as a pair of 4-byte floats. Some RTUs will instead return those as six 1-byte integers (MM/DD/YY followed by HH/MM/SS).
6-Byte Format Returns Day First
Enabled only when the preceding option is selected. Returns a 6-byte date format as DD/MM/YY instead of MM/DD/YY.
The following widgets are available to display information about your Enron Modbus driver tags: