Alarm API Structure Definitions
The alarm manager defines several data structures.
- The configuration structure is obtained and populated when commissioning an alarm. Alarm Configuration Structure
- The status structure may be obtained and monitored to watch for changes to an alarm's state. Alarm Status Structure
- The transaction structure contains information about an alarm event that is stored to the database including what changed (active state on or off...), the logged-on user, which workstation, etc. Alarm Transaction Structure
- The record structure is the complete set of information for each entry in the alarm database. This includes both configuration and transaction information. Alarm Record Structure
Every alarm can be described using a known configuration structure. When configuring a new alarm, this structure should be created via a call to \AlarmManager\GetAlarmConfiguration, then populated with the appropriate values before a call is made to \AlarmManager\Commission.
| ConfigurationStruct { All Boolean flags default to FALSE } | |
| Name |
Unique name for the alarm. Typically the unique ID. |
| FriendlyName | Display name of the alarm's source. |
| Area | Area |
| Description | Description. See also: NoLegacyAlarmDesc |
| Priority | Priority. Must be valid to be commissioned. Must be an integer corresponding to the Alarm Priority tag values. A priority of 0 will be treated as an event and will not go on either the Active or Current lists. |
| Reserved | |
| Disable | TRUE to disable the alarm. |
| DisableParmName | Name of the tag's disable parameter. Allows you to get the operator name who made the configuration change. |
| OnDelay | Seconds to delay before activating. |
| OffDelay | Seconds to delay before clearing. |
| RearmDelay | Seconds to delay before rearming after acknowledgment. |
| Setpoint | Setpoint of alarm evaluation. The value is compared against the setpoint. |
| ValueLabels | Array of labels to display instead of Value or Setpoint. Rarely used by tags other than digitals. |
| Units | Phrase Key of the setpoint units. |
| Function | Enumerated function for alarm evaluation. See: Alarm Manager Function Constants |
| AlarmType | String identifying the type of alarm. Used for display purposes only, in accordance with the ISA18.2 standard. Examples include "Low", "High", "Test". |
| Trip | TRUE if alarm only becomes unacked not active. |
| NormalTrip | TRUE if alarm becomes unacked when it clears. |
| OffNormal | TRUE if alarm only becomes active not unacked. |
| Deadband | Setpoint deadband. |
| PopupEnable | TRUE to enable popup display of active alarm. |
| SoundFile | Filename relative to app path of custom sound. |
| Custom | Number/String/Array/Dictionary/Structure containing custom data. This information is not shown anywhere on the AlarmPage by default, but could be displayed using a custom column. |
| AdHoc | TRUE if alarm is ad hoc. Should not be set explicitly. It is an internal flag that is set if the alarm object calls AdHocAlarm() rather than Commission() |
| ReactivateOnValueChange | If TRUE, the alarm will reactivate whenever the reported value changes. |
| DescPhraseID | PhraseID or a ParmPhrase structure to translate the description to current language. |
| NormalAck | TRUE to auto-ack the alarm when it clears. |
| DisplayInfo | Sub-structure of display information. For display only, not evaluation. |
GetAlarmConfiguration returns only a copy of the alarm's structure, not a reference. To update any property within the structure:
- Obtain a copy using GetAlarmConfiguration.
- Change values within that copy as required.
- Include the copy in a new call to the Commission function.
| AlarmStatus Struct | |
| IsActive | TRUE if alarm is on the Active list |
| IsUnacked | TRUE if alarm is on the Unacked list |
| IsShelved | TRUE if alarm is on the Shelved list |
| IsDisabled | TRUE if alarm is on the Disabled list |
This structure should be used in all new code, replacing the older functions IsActive, IsUnacked, IsShelved and IsDisabled.
| TransactionInfo Struct | |
| Name | Alarm name |
| Cfg | Alarm's configuration. Only required to bypass the alarm's commissioned configuration. |
| Action | Alarm action code that identifies the reason for the transaction. See following list. |
| Transaction | Alarm transaction string |
| Timestamp | Alarm timestamp (UTC) |
| Value | Tag value |
| Custom | Custom fields. Overrides Cfg\Custom |
| Reserved | |
| MachineID | Workstation's MachineID. Defaults to local. |
| AccountID | AccountID of operator |
| Device | Name of client device |
| ExpiryTime | Time the record is to be removed (UTC) |
| RemovalGUID | Reference GUID for targeted removals |
| NoteInfo | Structure containing information about a note that has been attached to this transaction. It provides the Timestamp and GUID of this transaction. |
The transaction string takes the form, "ListName+" or "ListName-". Several transactions can be combined in one string. The following example sets both the unacknowledged status and the active status off: "Unacked-Active-".
List names include the following: Active, Unacked, Shelved, Disabled, Configured.
Alarm Action Codes
Relates to "Action" in the Alarm Transaction Structure.
The action code is used for displaying a label in the "Event" column when viewing alarm history, and for filtering on specific kinds of historical events. The code is translated into a label by GetAlarmActionLabel().
The supported action codes are:
- Ack - alarm acknowledged
- Active - alarm became active and unacknowledged
- ActiveAck - alarm became active and acknowledged
- ClearAck - alarm became normal and acknowledged
- ClearTrip - alarm became normal and unacknowledged
- Commission - alarm commissioned
- Decommission - alarm decommissioned
- Disable - alarm disabled
- Enabled - alarm enabled
- Event - an event
- Modify - alarm modified
- Notified - alarm notification sent
- OffNormal - alarm became active without becoming unacknowledged
- Purge - orphaned alarm purged
- Rearm - alarm became active and unacknowledged again
- Recommission - alarm recommissioned
- Renamed - alarm renamed
- Shelve - alarm shelved
- Trip - alarm became unacknowledged
- Unshelve - alarm unshelved
AlarmRecord Struct |
| TimeStamp | UTC time for the event |
| GenTimestamp | UTC time when the record was written |
| GUID | 16 byte unique ID for the event |
| ReferenceGUID | GUID of original event that this cancels |
| ReferenceTime | Time when original canceled event occurred |
| Name | Alarm name, typically the tag name |
| Area | Alarm area |
| Transaction | List additions and deletions |
| Action | Alarm action to display for history event |
| Priority | Alarm priority (integer) |
| IsShelved | TRUE if this alarm is shelved |
| Database | UniqueID of the alarm database tag |
| Custom | Field to be used by OEM & app code |
| MachineID | Workstation where record originated |
| Device | Name of originating client computer |
| UserID | User associated with the event |
| Description | Alarm description/message |
| Reserved | |
| ExpiryTime | Time shelved record is to be removed |
| OnDelay | Time to wait (seconds) before activating |
| OffDelay | Time to wait (seconds) before clearing |
| Value | Tag value at time of alarm event |
| Setpoint | Alarm setpoint |
| Units | Setpoint units |
| Function | Setpoint function. See: Alarm Manager Function Constants |
| AlarmType | Type of alarm |
| SetpointLabel | Label to display instead of Setpoint |
| ValueLabel | Label to display instead of Value |
| RearmDelay | Rearm delay (seconds) |
| Deadband | Analog deadband |
| SeqNum | Sequence Number (for history sort) |
| Trip | TRUE if alarm was tripped |
| AdHoc | TRUE if alarm was ad hoc |
| NoteAttached | TRUE if one of more notes attached to record |
| IsConfig | TRUE if the alarm configuration is changed |
| IsReevaluation | TRUE if due to a reevaluation |
| UTF8 | TRUE if the record was stored with UTF8 encoding. Pre-multi-language records will not have this field in the packed records and this field will always be Invalid for those records. Used to determine if the record needs to translate fields to UTF8 upon reading. |
| DescPhraseID | PhraseID or a ParmPhrase structure to translate the description to current language. Pre-multi-language records will not have this field in the packed records and this field will always be Invalid for those records. |
| TagName | Text version of the tag name of alarm (i.e. not the GUID of the tag.) |
| Workstation | Text version of the workstation where record originated |
| UserName | Text version of the UserName associated with the event |
| PopupEnable | TRUE if the alarm is configured as a popup |